 Post subject: steam from elson tank
PostPosted: Fri Oct 30, 2009 8:39 pm 
Offline
User avatar

Joined: Fri Oct 30, 2009 8:38 pm
Posts: 2
there is an elson tank located in an airing cupboard, directly above a potterton kingfisher mf50rs boiler, the pump runs, all the rads heat up, the over heat stat and thermister have been checked yet whenever the boiler is left on for over an hour it srarts to produce steam from the elson tank, which fills the room! and sugestions on probable causes?

many thanks


Top
 Profile  
 
 Post subject: Re: steam from elson tank
PostPosted: Fri Oct 30, 2009 8:42 pm 
Offline
Site Admin
User avatar

Joined: Fri Oct 23, 2009 4:57 pm
Posts: 29
Possibly pumping over.

_________________
plumber in rochdale 01706 662013 for all plumbing - no job too small - lowest price garunteed - mr plumber - http://www.mrplumberonline.com


Top
 Profile  
 
 Post subject: Re: steam from elson tank
PostPosted: Fri Oct 30, 2009 8:43 pm 
Offline
User avatar

Joined: Fri Oct 30, 2009 8:38 pm
Posts: 2
considered this, pump was set on 2, dropped pump speed to 1 but still the same problem. the pump does look as though it has been changed at some point, is it possible that to big a pump has been fitted? any recomendations for pump size on a gravity hw / pumped ch system with arround 1.2m of head?


Top
 Profile  
 
 Post subject: Re: steam from elson tank
PostPosted: Fri Oct 30, 2009 8:43 pm 
Offline
Site Admin
User avatar

Joined: Fri Oct 23, 2009 4:57 pm
Posts: 29
Check the pump when fitted was not reversed (put in wrong way round) and is on lowest setting. When running, is water flowing from heating vent pipe, and if you can check heating cold feed for water movement (stick you hand in cistern) If its the vent pumping over it may be easier to extend the height of vent pipe than try to find an alternative pump. (assuming a standard circulater has been fitted. Good Luck

_________________
plumber in rochdale 01706 662013 for all plumbing - no job too small - lowest price garunteed - mr plumber - http://www.mrplumberonline.com


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC


Who is online

Users browsing this forum: No registered users and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
cron
Donate Now
Donate Now

Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group
Hosted by FreeForums.org | Create a free forum

SD_Chilean v2.0.3 desgined by SinDramas.com